Using SWA as CPC on a 25MM 4 CORE???

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

johnnymac

Junior Member
Joined
Apr 1, 2010
Messages
27
Reaction score
0
Hi can anyone help please? I have to upgrade an old (fuse) D/B to a new (MCB) D/B and the existing supply cable is a 25mm 4 core SWA, with the SWA being used as the CPC. The length of the run from the mains panel is about 40-50 mts.Is this acceptable or is a seperate cpc required ???

 
It's in GN1, however, is your Zs OK for the CPD?

I'll did out GN1 in a bit and see.

As this is 4c then it is a TPNE supply then?

---------- Post Auto-Merged at 20:49 ---------- Previous post was made at 20:31 ----------

GN1 says that the armour on a 25mm 4C BS6346 SWA is adequate to comply with table 54.7.

To make any further judgement you would need to know the CPD size.

 