It's ok lineman I went the day after and sorted it for yaHad this exact fault on a couple of weeks ago mate. Vacuum tripping rcd on one socket only. Removed socket from wall and neutrals popped out of terminals. Replacement socket and relevant testing and no complaint since.
Especially with a Neutral - Earth faultThere could be a small leakage to earth on that circuit due to a poor connection or damaged insulation which is below the RCD trip current, but when the vacuum is running, (a relatively high power appliance), the increased current causes more leakage across the poor joint or cable damage. It may be beneficial to have the RCD tested to verify it is not over sensitive.Doc H
PAT Test on fire L-E FaultGot a similar fault to go to on Mondaynew cct in new conservatory
plug an electric fire in and it trips rcd after 5 mins,,,,on one socket
nothing elses trips the rcd
one of two things,,,,,,
cable loose behind socket or fire faulty,,,,,,hope its the fire...
i can charge for it !!!!
---------- Post Auto-Merged at 23:40 ---------- Previous post was made at 23:38 ----------
I did also ask them to plug a kettle into the socket with a full load of water,,,,it didnt trip....