Hi,
A 10kw 230V Shower is supplied using PVC T&E Clipped Direct to surface over distance of 15m. Circuit Protected by BSEN60898 Type C. Ambient Temperature is 25 degrees c.
Reference Method C ?
10000/230 = 43.5A (rounded)
Breaker 45A Type C
Rating Factors 1.03 for 25 degree temperature, therefore 43.5/1.03 gives 42.23
Cable = Could use 6mm but its close so use 10mm for future upgrades.
Volt Drop - 10.0/4.00 is 6.44 (OSG)
This is where im stuck (if not gone wrong already)
6.44x(??43.5??)x15m
1000
=4.20V which is well less than the 5% allowed.
Ive bolded out the bit im mainly stuck on is this supposed to be the design current after or before rating factors have been taken into account
Thanks in advance for any help
Cheers
Matt