davetheglitz
Electrician
For the first time ever I've had a chance to play with a Voltage Operated ELCB. Gas bonding was required - and the customer refused to upgrade to an RCD. Decided to proceed with the recommendation that they upgrade to an RCD ASAP. Also couldn't see an earth rod anywhere - assumed it was earthed via a water pipe - so put one in.
What I thought was a bond to the water pipe was in fact a concreted in rod (somewhere) helpfully wired in 16mm meter tail. Since found out that the water came in on plastic.
With the two earth rods on one side of the coil and the CU with bonding on the other, it tripped out OK when I switched on my 15W soldering iron with the neutral wire in the earth pin on the plug (the only quick and dirty test I could think of - no-one else in the house!)
I always understood that you couldn't test voltage operated ELCBs with an RCD tester so could never verify correct operation - but my Fluke 1651 tripped it on 30mA in 116ms on x1 and in 16.5ms on x 5. Seemed fine! Ze was around 55 ohms (very good for down here!)
I know these devices finished in the early 80's - but to my mind they seem simple devices that do the job nicely as as long as the earth is connected.
Note that the system I was working on had 2 independent earth rods - the old concreted over one - and the new one I put in - so the chances of losing the earth would be minimal.
By the same token you can virtually disable an RCD in a TT system with a N-E fault - something that this system would not be susceptable to.
Anybody got any thoughts on why they are not used anymore?
What I thought was a bond to the water pipe was in fact a concreted in rod (somewhere) helpfully wired in 16mm meter tail. Since found out that the water came in on plastic.
With the two earth rods on one side of the coil and the CU with bonding on the other, it tripped out OK when I switched on my 15W soldering iron with the neutral wire in the earth pin on the plug (the only quick and dirty test I could think of - no-one else in the house!)
I always understood that you couldn't test voltage operated ELCBs with an RCD tester so could never verify correct operation - but my Fluke 1651 tripped it on 30mA in 116ms on x1 and in 16.5ms on x 5. Seemed fine! Ze was around 55 ohms (very good for down here!)
I know these devices finished in the early 80's - but to my mind they seem simple devices that do the job nicely as as long as the earth is connected.
Note that the system I was working on had 2 independent earth rods - the old concreted over one - and the new one I put in - so the chances of losing the earth would be minimal.
By the same token you can virtually disable an RCD in a TT system with a N-E fault - something that this system would not be susceptable to.
Anybody got any thoughts on why they are not used anymore?