Currently fitting electrical items along side rotary milking parlour fitters and we’ve came to a disagreement. The 3 drive motors are in the centre and require power to them. It’s all fed from a VSD now I didn’t know this at the time and have run 3 x SWA cables from
Plant room into centre through underground ducts. However, as it’s now apparent that it’s on a vsd, the fitter is asking that I remove my armours and run SY instead. Now normally I’d agree however I don’t particularly want to run an SY through and underground duct. So my question is as follows, if I run armour to the isolator then SY from there to the motor will that still stop the end effects or do I need to remove my armour and firnSY all the way.
Cheers
Bobby
Currently fitting electrical items along side rotary milking parlour fitters and we’ve came to a disagreement. The 3 drive motors are in the centre and require power to them. It’s all fed from a VSD now I didn’t know this at the time and have run 3 x SWA cables from
Plant room into centre through underground ducts. However, as it’s now apparent that it’s on a vsd, the fitter is asking that I remove my armours and run SY instead. Now normally I’d agree however I don’t particularly want to run an SY through and underground duct. So my question is as follows, if I run armour to the isolator then SY from there to the motor will that still stop the end effects or do I need to remove my armour and firnSY all the way.