Hi Slipshod,
British standards USED to say that the secondary windings of the set be earthed to the internals of the set, they then changed their mind for this precise reason.
See here for instance
Job knowledge for welders 28: Health, safety and accident prevention: electrical hazards - power source and installation
Note in particular the paragraph;
"In very old designs, the welding circuit was sometimes connected internally to the power source enclosure ( Circuit c). However, the danger is that even with the welding return lead disconnected, and a separate earth connection, welding is possible with current flowing through the earth. Because of the risk of damaging protective earth and other connectors, this type of power source is considered to be obsolete and should not be used"
Trust me, the welding institute know what they are talking about.
The sort of thing you describe was a very common [and well known] problem until the british standards people realised what was happening and changed their minds......
Most of us have done a bit of welding; How often have you tried to strike up, but nothing...a few moments of ehhhh, and then Doh, the welding return has come off.
Think if everytime this happened, the CPCs' in your entire installation got damaged.....
ANY welding set in which the secondary windings are not isolated from the CPC supplying the thing, [thus creating the problem] either;
1, Is obsolete
2, Is faulty
3, Does not comply with british standards.
Industrial welding sets are SERIOUS bits of kit. I have a welder not 20 feet from me as i write this; It is not a particularly big one, but it is rated to churn out 260 Amps, 100% CONTINUOUSLY or, 320 Amps 60% of the time, or 350 Amps 50% of the time..
In welding "duty cycle" terms, this is 5 minutes of welding with a 5 minute break.
This thing requires minimum 50mm csa welding cable... So, unless all the CPC's in your installation are 50mm csa [make your "black and decker" a bit difficult to handle!!] guess what is going to happen the first time you forget to connect the welding return cable...
The sad fact is, the person that wrote the article you quoted from may well be the best electrician in the whole world. The fact is, they know NOTHING of welding machinery.
How can i say this??? It is a question of the very "telling" sentences;
"Inspection of several welder earth clamps found overheated cable ends where the connection to the clamp was made"
and
"In the average welding shop, the earth clamps tend to be tatty, bad or loose connections from the earth lead to the clamp"
No such thing as a "welder earth clamp"... It is a "welding return cable" This is not me being "pedantic", a "welding earth" is a VERY different thing.
Think of this; would you employ an electrician that either did not know the difference between "earthing" and "bonding" or used the two terms "interchangeably" or thought that anyone that did not call "bonding" "earthing" was being pedantic....
john...
British standards USED to say that the secondary windings of the set be earthed to the internals of the set, they then changed their mind for this precise reason.
See here for instance
Job knowledge for welders 28: Health, safety and accident prevention: electrical hazards - power source and installation
Note in particular the paragraph;
"In very old designs, the welding circuit was sometimes connected internally to the power source enclosure ( Circuit c). However, the danger is that even with the welding return lead disconnected, and a separate earth connection, welding is possible with current flowing through the earth. Because of the risk of damaging protective earth and other connectors, this type of power source is considered to be obsolete and should not be used"
Trust me, the welding institute know what they are talking about.
The sort of thing you describe was a very common [and well known] problem until the british standards people realised what was happening and changed their minds......
Most of us have done a bit of welding; How often have you tried to strike up, but nothing...a few moments of ehhhh, and then Doh, the welding return has come off.
Think if everytime this happened, the CPCs' in your entire installation got damaged.....
ANY welding set in which the secondary windings are not isolated from the CPC supplying the thing, [thus creating the problem] either;
1, Is obsolete
2, Is faulty
3, Does not comply with british standards.
Industrial welding sets are SERIOUS bits of kit. I have a welder not 20 feet from me as i write this; It is not a particularly big one, but it is rated to churn out 260 Amps, 100% CONTINUOUSLY or, 320 Amps 60% of the time, or 350 Amps 50% of the time..
In welding "duty cycle" terms, this is 5 minutes of welding with a 5 minute break.
This thing requires minimum 50mm csa welding cable... So, unless all the CPC's in your installation are 50mm csa [make your "black and decker" a bit difficult to handle!!] guess what is going to happen the first time you forget to connect the welding return cable...
The sad fact is, the person that wrote the article you quoted from may well be the best electrician in the whole world. The fact is, they know NOTHING of welding machinery.
How can i say this??? It is a question of the very "telling" sentences;
"Inspection of several welder earth clamps found overheated cable ends where the connection to the clamp was made"
and
"In the average welding shop, the earth clamps tend to be tatty, bad or loose connections from the earth lead to the clamp"
No such thing as a "welder earth clamp"... It is a "welding return cable" This is not me being "pedantic", a "welding earth" is a VERY different thing.
Think of this; would you employ an electrician that either did not know the difference between "earthing" and "bonding" or used the two terms "interchangeably" or thought that anyone that did not call "bonding" "earthing" was being pedantic....
john...