Hi,
I finally succumb to better judgement and dared to pull out one of the 2.5 t&e cables to my workshop which ran 16 meters in 50mm conduit. I have another to pull out now but I want to use it to drag through some armoured instead. This way I can forget the need for an RCD at head end and not have to worry about discrim.
Also means I can up the power to the workshop.
Keeping in mind I have two bends to pull this stuff through, what swa size would be realistic for:
2 x 16A radials
1 x 3A lighting (Mainly LED lamps, but total wattage is only around 120W)
1 x 3A fire/intruder alarm
The two radials will be on RCBOs, possibly the lights also. The alarms unprotected. (Anyone RCBO/RCD alarms on dedicated circuits?)
Realistically max continuous load would never be over 1.5Kw on each radial, of course there might be a rare occasion a 1Kw fire gets put on but I have a balanced flue gas heater partly for that reason.
I was hoping to get away with 6mm2 / 3 core?
I finally succumb to better judgement and dared to pull out one of the 2.5 t&e cables to my workshop which ran 16 meters in 50mm conduit. I have another to pull out now but I want to use it to drag through some armoured instead. This way I can forget the need for an RCD at head end and not have to worry about discrim.
Also means I can up the power to the workshop.
Keeping in mind I have two bends to pull this stuff through, what swa size would be realistic for:
2 x 16A radials
1 x 3A lighting (Mainly LED lamps, but total wattage is only around 120W)
1 x 3A fire/intruder alarm
The two radials will be on RCBOs, possibly the lights also. The alarms unprotected. (Anyone RCBO/RCD alarms on dedicated circuits?)
Realistically max continuous load would never be over 1.5Kw on each radial, of course there might be a rare occasion a 1Kw fire gets put on but I have a balanced flue gas heater partly for that reason.
I was hoping to get away with 6mm2 / 3 core?