Hi, 4kw solar system, 5.8kw solax inverter coupled to 1 x 5.8kw battery. Fitted October 2023 10mm cable from inverter to consumer unit.

Currently have wylex NHXS1B40 Fitted which has been fine until we have rain then trips. I have been on roof and all connectors seem ok. if you isolate panels its fine. Can anyone confirm which RCD should be fitted and link to buy the correct one if not.

Thanks
 
If it only trips when it rains, suggests the problem is moisture ingress is tripping the RCBO.

Best to call the installers back as its less than 6 months since installation
 
Moisture Ingress ? Arent MC4's fully waterproof ?
If fitted properly they can be immersed in a puddle to a depth of 1m. However, many installers seem to lack MC4 spanners needed to do them up properly, or overtigten and cross thread them. Some factory fitted connectors aren't always great, and a favourite of any seal leaking is getting dirt on them.
 