Moving a double socket along a wall a short distance so it wont be hidden behind proposed fitted wardrobes...
(pencil line down wall edge of new wardrobe).
Back box prep all done.. so a give a gentle tug on each of the legs of the ring to see if either has enough slack to reach the new position without a J/box..
As I pull on one cable.. hear a bang, see a spark from below the floor boards!
(32A MCB trips.. not RCD)
Roll a bit more carpet.. lift another board.. And what do we find...
Cable passing though a joist.. with a bit a black charring around the hole...
Look back at lifted board.. Note nail position.......
(and black charring on underside of board..)
So whoever put that nail in managed to pierce both cables...
I wonder..... did the Fuse/MCB, pop.. and they just replaced/reset it?
OR.. was it just a fluke that nothing happened till I gave it that 'Extra Tug', AKA the straw that broke the camels back?
Close up on the removed section of cable...
Oh and yes..
for those our our "eagle-eyed" forumbulator members..
That IS a section of Lead Gas Pipe running under the board I lifted..
(The customer thinks this may still be a live gas supply.. as his downstairs gas fire was also via lead pipe until some relatively recent gas alterations work..
BUT.. requires someone still specially trained to work with lead-pipe to sort it out!)
So...
how long has this fault-in-waiting.. actually been Waiting?????
Answers on a postcard to..
"And that's why the regs state 50mm depth for cables passing though joists"
PO BOX 522.6.201
(pencil line down wall edge of new wardrobe).
Back box prep all done.. so a give a gentle tug on each of the legs of the ring to see if either has enough slack to reach the new position without a J/box..
As I pull on one cable.. hear a bang, see a spark from below the floor boards!
(32A MCB trips.. not RCD)
Roll a bit more carpet.. lift another board.. And what do we find...
Cable passing though a joist.. with a bit a black charring around the hole...
Look back at lifted board.. Note nail position.......
(and black charring on underside of board..)
So whoever put that nail in managed to pierce both cables...
I wonder..... did the Fuse/MCB, pop.. and they just replaced/reset it?
OR.. was it just a fluke that nothing happened till I gave it that 'Extra Tug', AKA the straw that broke the camels back?
Close up on the removed section of cable...
Oh and yes..
for those our our "eagle-eyed" forumbulator members..
That IS a section of Lead Gas Pipe running under the board I lifted..
(The customer thinks this may still be a live gas supply.. as his downstairs gas fire was also via lead pipe until some relatively recent gas alterations work..
BUT.. requires someone still specially trained to work with lead-pipe to sort it out!)
So...
how long has this fault-in-waiting.. actually been Waiting?????
Answers on a postcard to..
"And that's why the regs state 50mm depth for cables passing though joists"