Why are you taking up the floor now, when it sound like you've narrowed the leak to the boiler? Unless you are dead unlucky you won't have TWO leaks.
Just worked out how to quote, dah! forgot how to.Unless you really like pulling floors up I'd have turned off the boiler, closed isolator valves (or removed and linked the boiler flow and return pipes) with a gauge in line and pressurised that arrangement to 2 bar. If it held its not the external piping
Otherwise/then close/cap the boiler return put 2 bar into the flow and again pressurise and check. remember that a leak inside the combustion chamber can exit invisibly down the condensate drain
Don't over think it - just narrow it down !!
If the gauge is on the boiler, (which is the normal arrangement), then it's monitoring the pressure in the boiler and if it still falls with the isolator valves shut then that's where your problem is; i.e. within the boiler.Just worked out how to quote, dah! forgot how to.
Isolating valves was mentioned way back at start of topic, just wasn't sure exactly whether I should shut off all 4, have mobility issues and struggled to get under and shut all 4 off but managed okay.
I'm assuming I now wait to see if pressure drops over a period of time? and if stays at same pressure, it is not a boiler leak issue?