Well I got the job because the lady of the house put her foot down & I was recomended by her mate. Her hubby on the other hand wasnt overly chuffed at the £400 quote.
Quoted for out with the old cu 7 way 3036, move new cu a few feet/extend circuit tails & install MEB as none present to gas & water.
I get there & matey pipes up over a brew
"one of the lads I know said he would do it for £100, he did his own swap a few months ago & the board only cost him £60 from toolstation"
Is he a sparks then?
"No , but he is good with diy stuff"
So I crack on & this simple board change becomes a 09:30 to 19:00 mare.......(did IR & ring cont during quote visit)
Upstairs lighting only partrial cpc continuity on the circuit.......(traced to diy bob and all cpc's cut off at a jb.....bathroom ligts) loft fully boarded over all cables/jb's & DL's.
Multiple spurs off spurs (lucky they were all in the garage so put on their own circuit on new board)
Kitchen socket x4 wired in 1.5mm off 32A down ringmain (had a break as it was wired back to the board, so plonked in on it's own 20A radial via a fused spur next to cu).
Has to be said the blokes attitude changed by the end of the day....................
"you've earned your money mate, I had no idea what was involved. "
Hmm bet your mate would have slapped the new unit in, no testing, no rectification work, no testing, no cert, no warranty, no hope of it being safe...............................but you would have saved a couple of hundred quid.
"Sorry I questioned the price you put in, Use this £20 to buy a beer on the way home"
Quoted for out with the old cu 7 way 3036, move new cu a few feet/extend circuit tails & install MEB as none present to gas & water.
I get there & matey pipes up over a brew
"one of the lads I know said he would do it for £100, he did his own swap a few months ago & the board only cost him £60 from toolstation"
Is he a sparks then?
"No , but he is good with diy stuff"
So I crack on & this simple board change becomes a 09:30 to 19:00 mare.......(did IR & ring cont during quote visit)
Upstairs lighting only partrial cpc continuity on the circuit.......(traced to diy bob and all cpc's cut off at a jb.....bathroom ligts) loft fully boarded over all cables/jb's & DL's.
Multiple spurs off spurs (lucky they were all in the garage so put on their own circuit on new board)
Kitchen socket x4 wired in 1.5mm off 32A down ringmain (had a break as it was wired back to the board, so plonked in on it's own 20A radial via a fused spur next to cu).
Has to be said the blokes attitude changed by the end of the day....................
"you've earned your money mate, I had no idea what was involved. "
Hmm bet your mate would have slapped the new unit in, no testing, no rectification work, no testing, no cert, no warranty, no hope of it being safe...............................but you would have saved a couple of hundred quid.
"Sorry I questioned the price you put in, Use this £20 to buy a beer on the way home"