When fitting a DB, ie an install, measuring the Ze the correct GN3 way is fine, but measuring Ze during a condition report is not. During a periodic you are supposed to switch everything off, then pull out the earthing conductor from the MET and then test, ensuring no pararllel paths. GN3 also says carry out your tests with minimum dismantleing and dissruption. Getting a GN3 style Ze on say a health centre or call centre would be very dissruptive. Imagine announcing you are having to shut the buildings electrics down while you make the test. Staff and others may have to vacate the premises for H&S reasons or rely on emergency lights while all the computers shut down.
GN3 says that measuring Ze will be easier than using the DNO enquiry values ( if you can get them). I have been in many buildings while contractors have been doing periodic testing and i have never known them to switch off the supply, but just take the measurement with all the circuits energised and the bonding etc still connected, as do I in that situation. Can you just enter 0.35 as standard without measuring on a TNCS and 0.8 on TNS?. The situation is rediculous. You basically get forced to cut corners for inconvenience sake and them someone who doesn't have to do the test themselves will say you have done the test incorrectly.
Not including the above tests I think the whole testing world is a farce. Very few test sheets i see are ever filled in correctly and the testers dont have a clue about many regs at all.
When doing periodics, you should be allowed to enter Ze with all conductors connected, and then a Zs.
The other method Zs = Ze + (R1+R2) relies on Ze.
GN3 says that measuring Ze will be easier than using the DNO enquiry values ( if you can get them). I have been in many buildings while contractors have been doing periodic testing and i have never known them to switch off the supply, but just take the measurement with all the circuits energised and the bonding etc still connected, as do I in that situation. Can you just enter 0.35 as standard without measuring on a TNCS and 0.8 on TNS?. The situation is rediculous. You basically get forced to cut corners for inconvenience sake and them someone who doesn't have to do the test themselves will say you have done the test incorrectly.
Not including the above tests I think the whole testing world is a farce. Very few test sheets i see are ever filled in correctly and the testers dont have a clue about many regs at all.
When doing periodics, you should be allowed to enter Ze with all conductors connected, and then a Zs.
The other method Zs = Ze + (R1+R2) relies on Ze.