Lyngarth

Member
Joined
Aug 7, 2009
Messages
84
Reaction score
0
hi,

Sorry for the silly queston but was just checking what the max zs is on a 32amp breaker. Just checking a ring before adding 2 more scokets, but all my books are in back on van, which my mate has and not back for 2 hrs.

Cheers

System is TT plus also max on 6amp lighting if you would be so kind.

 
BS 60898 MCB bud? if so its 1.16ohms (32amp) & 6.18ohms (6amp)AndyGuinness
Hi, yes thats the one, cheers for that.

Sadly just tested the ring and got 14.89 ohms.

So not going to be a quick 10 minute job by the looks of it.

Thanks for your reply.

 
But......it`s a TT.

You`ll hardly ever comply with max Zs for disconnection times on a TT - the Ra is too high. This is the reason for using a 30mA RCD - the disconnection time in the event of a fault is provided by the RCD, NOT the CPD.

HTH

KME

 
hi,

so seeing as the board has a rcd, is it ok to fit the new 2 sockets ??

Not sure myself, and this is my first tt system in 2 yrs!!

 
many thanks, will now put down the coffee and get to work.

Cheers to all for taking time to reply.

Lyngarth

 
Zs of 1666.66 ohms will comply with 50 Volt max touch voltage requirement fot TT.

 
Just 30mA mate (R=V/I) ;)

Lyn - ensure it IS a 30mA - some of the older TT installs had a 100mA "front end" instead!

Don`t forget, you also need to test the RCD for correct operation within time limits at 15mA, 30mA and 150mA; on both pos & neg halves of the waveform ;)

KME

Pushy ruddy shovey headbang

:^O :^O:ApplaudGuinness

 
Just 30mA mate (R=V/I) ;) Lyn - ensure it IS a 30mA - some of the older TT installs had a 100mA "front end" instead!

Don`t forget, you also need to test the RCD for correct operation within time limits at 15mA, 30mA and 150mA; on both pos & neg halves of the waveform ;)

KME

Pushy ruddy shovey headbang

:^O :^O:ApplaudGuinness
or even a voltage trip, :eek:

 
Hi

Job now done, I checked the RCD and it was a 30ma, and tested fine.

Have also made sure from now on my books stay with me.

Cheers all

Lyngarth

 