Today I was working on my last job before retirement, still plenty to do though.
Anyway, next door asks me if I can have a look at his house as when he resets his rcd his neighbours trips.
Don't want to get involved but a quick look found the following.
Originally the property was one house and converted to two.
Both TT but no sign of any rods.
Incoming supply has been split to separate meters.
House A has a 30mA rcd at the front end.
House B has 100mA at the front end.
House B rcd tripped, first time he can remember in years.
When he reset the rcd House A rcd tripped. House A resets no problem.
I tried this several times with the same result.
If I pull the 5A lighting rewirable fuse from House A then reset house B there is no tripping.
Oddly enough house B has one light which is supplied from House A.
Definitely not getting involved with this but your thoughts please.