Hi
so I've just had another EICR done and while I was expecting some of the required remdial works - which include a new CU and gas meter earth bond - the electrician has added another item which they didn't mention when they were on site to the required works.
They are saying in addion to a new RCBO consumer unit with surge protectin within the property that the supply going from the meter (which is in a communal hallway) to the flat requires another RCD.
They say this is because it is "twisted pair" wiring and isn't in steel trunking. I note that none of the other properties in the block have any such RCD in the hallway cupboard depsite many of them being rented out.
I've asked my electrician if this is actually in scope as it says on the report that the EICR covers "all power and lighting circuits emanating from consumer unit only". To me this means downstream of the CU. But speaking to the electrician he says i am responsible for the supply from the meter onwards. It seems to me he is testing and upgrading something that is outside the self defined scope of the EICR and that either the scope should be increased or the extra RCD requirement disregaded or perhaps relayed to the managing agents of the block.
On a side point he has also put in the field saying next inspection due in " Every 5 years or time tenancy changes whichever is sooner". The "tenancy changes" requierement seems totally OTT to me and is potentially just profiterring.
I'd be interested to get others opinions on the above
so I've just had another EICR done and while I was expecting some of the required remdial works - which include a new CU and gas meter earth bond - the electrician has added another item which they didn't mention when they were on site to the required works.
They are saying in addion to a new RCBO consumer unit with surge protectin within the property that the supply going from the meter (which is in a communal hallway) to the flat requires another RCD.
They say this is because it is "twisted pair" wiring and isn't in steel trunking. I note that none of the other properties in the block have any such RCD in the hallway cupboard depsite many of them being rented out.
I've asked my electrician if this is actually in scope as it says on the report that the EICR covers "all power and lighting circuits emanating from consumer unit only". To me this means downstream of the CU. But speaking to the electrician he says i am responsible for the supply from the meter onwards. It seems to me he is testing and upgrading something that is outside the self defined scope of the EICR and that either the scope should be increased or the extra RCD requirement disregaded or perhaps relayed to the managing agents of the block.
On a side point he has also put in the field saying next inspection due in " Every 5 years or time tenancy changes whichever is sooner". The "tenancy changes" requierement seems totally OTT to me and is potentially just profiterring.
I'd be interested to get others opinions on the above