Not sure what age the building is, but I would say 1980s. The lighting is all wired in double insulated singles. The lines have a CPC, the neutral doesn't. So I'm trying to think if that really meets current standards given that we regard the neutral as a live conductor. Your thoughts please
 

Attachments

  • IMG_20240530_102958.jpg
    IMG_20240530_102958.jpg
    2.4 MB
You can still buy it like that the one with the cpc is 6241Y and without is 6181Y.
 
Although the neutral conductor carries current and is deemed live it's potential is low.
 
Few years back we rewired an office floor using this stuff. Don't know what was going through the designer's mind but looked good in the ceiling void, it was all strung through spacer bar saddles so imagine a conduit system without the conduit!
 
Few years back we rewired an office floor using this stuff. Don't know what was going through the designer's mind but looked good in the ceiling void, it was all strung through spacer bar saddles so imagine a conduit system without the conduit!
I guess that's the main joy of it, especially compared to steel conduit - I'm trying to think when pvc became the norm?
 