HappyHippyDad
Well-known member
Finding a fault on a tripping RCD is usually fairly straight forward. The fault usually shows up on an IR test, then we just break the circuit down.
However, with a tripping MCB I find it harder.
We know that a 30mA RCD will trip (approx) with a L/N -E IR of around 8000ohms or below (I'm being very simplistic here, I realise the figure can be much higher as it changes very easily. the point being we have an idea of what to look for) , so we have a figure to keep in mind when testing. Is there a figure we are looking for when an MCB trips, or are we simply looking for continuity?
The reason I find it difficult, is because it can be sometimes impossible to remove all plugged in appliances/FCU's from the offending circuit, meaning we are always going to get a fairly low resistance figure between L and N, sometimes extremely low, low enough to indicate continuity, meaning an IR test for a tripping MCB is not a useful tool for finding the fault (as it is with a tripping RCD). Also, we wouldn't even know if we have removed everything, as there will always be a low resistance figure between L-N because we have a fault.
What are your go to methods for finding the fault linked with a tripping MCB?
I am assuming its not overload as this can be determined by working out max demand. Also, not a L-E fault as this could be found with IR testing. Purely a L-N fault/short circuit.
However, with a tripping MCB I find it harder.
We know that a 30mA RCD will trip (approx) with a L/N -E IR of around 8000ohms or below (I'm being very simplistic here, I realise the figure can be much higher as it changes very easily. the point being we have an idea of what to look for) , so we have a figure to keep in mind when testing. Is there a figure we are looking for when an MCB trips, or are we simply looking for continuity?
The reason I find it difficult, is because it can be sometimes impossible to remove all plugged in appliances/FCU's from the offending circuit, meaning we are always going to get a fairly low resistance figure between L and N, sometimes extremely low, low enough to indicate continuity, meaning an IR test for a tripping MCB is not a useful tool for finding the fault (as it is with a tripping RCD). Also, we wouldn't even know if we have removed everything, as there will always be a low resistance figure between L-N because we have a fault.
What are your go to methods for finding the fault linked with a tripping MCB?
I am assuming its not overload as this can be determined by working out max demand. Also, not a L-E fault as this could be found with IR testing. Purely a L-N fault/short circuit.