Good morning all.
I have just done a small job, during which I noticed all the cable is imperial cable (meaning 50+ years old)
No green goo. Global IR test 0.1Mohms (L/N - E).
When do you guys suggest a rewire?
The 0.1Mohms may well just be rust/rodent damage/damp etc etc.
If I fix the fault and the IR tests are >1Mohm, I would then suggest to the customer that they start considering a rewire, rather than saying they really need one.
Is this similar to what everyone else suggests?
I would start by saying that you have noticed the installation is quite old and there is no label at the CU identifying when it was last inspected and tested to confirm its safety for continued use... (re: 514.12.1)
Then ask them when it was last fully tested and do they still have copy of the inspection report?
If they either have no idea or it is known to be longer than 10years...
I would be recommending a comprehensive inspection and test of the whole installation, including IR's on individual circuits, not just global IR, ASAP.. as there could be potential problems..
(Also point out this could easily be a full days labour on an average domestic dwelling with no previous certificates / documentation available.)
Once you have some accurate tests results for the whole installation circuit by circuit, you are then in a position to identify what areas are due for remedial works / replacement to ensure the safety of persons using the installation.
I would never be suggesting anything needs rewiring without first reviewing some accurate records of circuit composition and test readings.. It is not uncommon for older installations to have various circuits, (parts of circuits), with wiring that is much newer following earlier building alterations etc.. and so does not require replacement yet.
If I ever come across IR test readings in single figures on an individual circuit that tends to start alarm bells in my book!
Even on some very old wiring I have know double digit 20 or 30meg+ IR @ 500v across all conductors.
Also don't forget older installations without RCD's at the CU may well have socket outlets with RCD's built in further down the circuits which can mess up your global IR readings.
What was the IR for the circuit you were doing your minor works on?