Wago wiring correctly
Stevie R
Nov 19, 2024
5
Lancashire
I am putting up some new light fixtures and am going to use ‘Wago’ connectors my question is I have a live, neutral, earth coming out of the ceiling and the same from the light fitting,
When wiring to the wago connector do the 2 live go together same with neutral, earth? I’ve attached a photo bit basic but hope it explains what I mean
Moved from "Electricians Talk Forum"
    1.1 MB
I Just need to know what wires go into a wago connection in terms of the L,N,E do you use 3 separate wago connectors then?
Each conductor the live, neutral and earth need separate connectors so you need three of them not just one or it will just create a dead short.
For your example you would need 3x 2way wago connectors..
https://www.tlc-direct.co.uk/Products/WA412C.html
Or personally for connections to light fittings I prefer these
https://www.tlc-direct.co.uk/Products/WA101.html
or if you need to loop in & out plus the light fitting
https://www.tlc-direct.co.uk/Products/WA112.html
Regulation 526.5 requires that every termination is either within a suitable accessory, equipment enclosure...
(Such as the boxes you mention...)
OR.. "An enclosure partially formed or completed with building material which is non-combustible when tested to BS 476-4"
Which is why many light fittings come with a metal bar screwed to the ceiling, or wall...
and a screw terminal block attached to the inside of the wall/ceiling rose cover plate that is later fixed to the ceiling/wall bar..
So the joints are just enclosed between the ceiling/wall plaster and the light fitting rose cover plate...
All good with 526.5 (iii)