  1. frankie310581

    Rcbo trip test

    as I was thinking the pir? ok but how do you get round this on the cert as the pir will be in circuit under normal use
  2. frankie310581

    Rcbo trip test

    there is a pir on the lights do you think it could be that it's all I can think of
  3. frankie310581

    Rcbo trip test

    tested at rcbo and end of circuit got the same
  4. frankie310581

    Rcbo trip test

    rcbo type b 6 amp feeding to lights ramp test 25ma 1/2 test >1999ms 1x test 32.4ms 5x test >40ms anyone now what can be causing the 5x test to fail Rcbo has been changed and it is still the same banging my head
  5. frankie310581

    Suspicious or not??

    Dobermans and shotguns it the way they get the point to stay well away
  6. frankie310581

    Suspicious or not??

    be careful mate sounds Like he got a stolen one and is cloning yours eg making his a double of yours eg reg so his dose not show up as stolen on the police car cameras look out for speeding fines and stuff
  7. frankie310581

    rcbo and zs

    I understand that but just trying to find out if there is a bad earth path our is the circuit if fine and it just the rcbo (pice of mind ) hope you get where we are coming from
  8. frankie310581

    rcbo and zs

    I WILL LET YOU NOW IT IS A STRANGE ONE ---------- Post Auto-Merged at 21:58 ---------- Previous post was made at 21:54 ---------- That is what i was thinking at first but all 11 circuits were the same all being rcbos very high zs readings
  9. frankie310581

    rcbo and zs

    Lol in a way yes lol but as above post elecsa said its ok and down to rcbos do you have any ideas
  10. frankie310581

    rcbo and zs

    X1= 28.3 x5= 8.5 no other tester has been used but all circuits are the same thay are dormen smith rcbos never used these before teaster is ok as teasted mcbs and had the right results this one has got me ---------- Post Auto-Merged at 21:38 ---------- Previous post was made at 21:36...
  11. frankie310581

    rcbo and zs

    Ze = 0.21 zdb = 0.27 r1+r2 = 0.31 COOKER zs = 22.3 this was just one of the 18 circuits giving the same very high zs this i have been told by elecsa tec line is down to the rcbos dont you think rcbos should come with a resistance value our would a resistance test from one side of the line...
  12. frankie310581

    Danger !!!!

    that being left anywhere never mind in a school is in my eyes attempted murder
  13. frankie310581

    supply companys info

    i no that feeling to well andy they told me at school years ago that i had a sort attention span too lolROTFWL now a days thay call it dyslexia but you lean to live with it lol
  14. frankie310581

    supply companys info

    :Csorry if that offended anyone but i was taking the mikey out of myself for not being good at english god i must be bad if that was not clear
  15. frankie310581

    supply companys info

    i wish i could sorry about that springcrocus but we can not be good at everything and we all have are downsides and punctuation and spelling is my biggest lol and yes i am english born and bread just in case you thort i mit be polish if you did i can see y iam bad lol
  16. frankie310581

    supply companys info

    like i said in the last post i no we can test for it and recongnize what it is from years of experiance and y would you bother ringing up for ze and pfc any way as they will only give you max permited for the supply type stated in the regs and like in many installations i have come across where...
  17. frankie310581

    supply companys info

    its wrong thay should have a data base on all installations via the postcode on the internet then we would not have to bother them and y we are on it we should all have main fuse seal kits with are reg number on it as 99% of job need upgrading to 25mm tails
  18. frankie310581

    supply companys info

    way is it so hard to find out of supply company what supply characteristics is at the property ie tns tncs tt 3phase single phase current / they never no our is it ringing the phone number o i now we can do by testing it ourselves but in some cases we can not like the job i am on at the mo due...