This first one is from a local school, picked up on 2 periodics 5 years apart. circuit is live at time of picture taken.
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00657.jpg
I was asked what could be done, so this is my temp fix having used wagos to terminate conductors.
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00658.jpg
These two are again a live circuit, when I arrived they were still using the left hand outlet to run a daisy chain of 3x trailing leads that were inturn powering.... 4x laptops - 1x 64 inch plasma - 1x overlay smart screen - 1x water chiller - 1x electric heater - 1x hot drinks machine.
Guess who the customer is & the department (spark999 is the clue).
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00660.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00659.jpg
The offending trailing lead.
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00661.jpg
These ones are from the same customer as above & show a trailing lead made up by somebody with a little knowledge ....... "we must have an rcd to protect the public" :Applaud . It was given to me to repair as the rcd wasnt working :^O
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00664.jpg
whats wrong here then
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00662.jpg
Oh that'll be it the load is 28amp.
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00663.jpg
The lead was in use to provide power to an interactive community vehicle when it was parked in a town centre.
Why not use the on board genny that provides the required 28amp.......because it is noisy when in the town giving advice to the public, so we plugged into a 3 pin socket in one of the shops. headbang
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00657.jpg
I was asked what could be done, so this is my temp fix having used wagos to terminate conductors.
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00658.jpg
These two are again a live circuit, when I arrived they were still using the left hand outlet to run a daisy chain of 3x trailing leads that were inturn powering.... 4x laptops - 1x 64 inch plasma - 1x overlay smart screen - 1x water chiller - 1x electric heater - 1x hot drinks machine.
Guess who the customer is & the department (spark999 is the clue).
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00660.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00659.jpg
The offending trailing lead.
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00661.jpg
These ones are from the same customer as above & show a trailing lead made up by somebody with a little knowledge ....... "we must have an rcd to protect the public" :Applaud . It was given to me to repair as the rcd wasnt working :^O
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00664.jpg
whats wrong here then
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00662.jpg
Oh that'll be it the load is 28amp.
http://i83.photobucket.com/albums/j293/gazjothomas/fire%20stations/DSC00663.jpg
The lead was in use to provide power to an interactive community vehicle when it was parked in a town centre.
Why not use the on board genny that provides the required 28amp.......because it is noisy when in the town giving advice to the public, so we plugged into a 3 pin socket in one of the shops. headbang