1.5mm earth singles for 2.5mm 3 phase 16A socket circuit?

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

sparky marky

Junior Member
Joined
Nov 29, 2010
Messages
6
Reaction score
0
My question is, is a 1.5mm singles earth conductor adequate for a 3-phase and neutral 16A 'ludent' socket wired in 2.5mm on a 16A fuse?

One 16A socket per circuit

 
Unless you want to use an adiabatic eq to prove its ok then it should be 2.5mm

 
Use 2.5 for compliance with table 54-7 or as above calculate using adiabatic equation - cheers

 