why do you say that, I think you have been given good advice, amongst other things.So,asking a simple question on here was obviously a big mistake :facepalm:
why do you say that, I think you have been given good advice, amongst other things.So,asking a simple question on here was obviously a big mistake :facepalm:
The good advice I take...its the other things :slap
I will have a go.Where does 411.4.4 and 531.3.1 come in?
I will have a go.
531.3.1 is relevant to only part of a TN system, ie to a certain piece of equipment. it is not relevant to the origin of the installation (531.4.1 refers to the "origin" in TT systems)
You have fitted a TD 100mA rcd just downstream of the meter. This does not provide shock protection, overload protection nor fault protection between L and N. It only gives some protection against fire. 411.4.4 says if an RCD is used in a TN system an ocpd is also required. The DNO's ocpd can't be used to "protect" your cable if over 3metres. You will have to fit your own.
so your 0.54 reading for 80A does seem ok.EDFs maximum figure for 100A supplies with a BS161 fuse is 0.38 ohms.
For 80A 0.52Ohms
For 60A 0.73 Ohms
For 45A 1 Ohms
For 30A 1.92 Ohms
For 20A 2.93 Ohms
For15A 5.22 Ohms
For 5A 17.1 Ohms.
Canoeboy said:You mean on the internet for your photo of the front page :slap ......
Sounds painful, you should get someone to inspect that fpr you.I have a green one,