13A Socket on a lighting circuit.

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
I am only assuming so don’t shoot me down, but isn’t it the responsibility of the designer to ensure that the cable is sufficient for the load, and 1.0mm can be used to supply an extractor fan in the kitchen for example so technically it now relies on the definition of ‘power’, so given that those that use the regs are supposed to be competent then we should hope that applied knowledge is used?
 
I am only assuming so don’t shoot me down, but isn’t it the responsibility of the designer to ensure that the cable is sufficient for the load, and 1.0mm can be used to supply an extractor fan in the kitchen for example so technically it now relies on the definition of ‘power’, so given that those that use the regs are supposed to be competent then we should hope that applied knowledge is used?
The previous Table 52.3 had a note to the lighting section regarding fans and the like but the new Table now incorporates power and lighting in the same part with 1.0 as the minimum copper size so no note required.. So connect whatever you will to a 1.0 circuit.
 
The previous Table 52.3 had a note to the lighting section regarding fans and the like but the new Table now incorporates power and lighting in the same part with 1.0 as the minimum copper size so no note required.. So connect whatever you will to a 1.0 circuit.

32A hot tub sounds good.o_O
 
The previous Table 52.3 had a note to the lighting section regarding fans and the like but the new Table now incorporates power and lighting in the same part with 1.0 as the minimum copper size so no note required.. So connect whatever you will to a 1.0 circuit.
Yes providing it is designed accordingly?
 
basically, we have gone back to 17th, which was 1mm for lighting & power. not sure when it changed (dont have 17th amd 1 or 2 here to check) but it was 1.5 for power in 17th amd3 & 18th
 
basically, we have gone back to 17th, which was 1mm for lighting & power. not sure when it changed (dont have 17th amd 1 or 2 here to check) but it was 1.5 for power in 17th amd3 & 18th
The original 17th Ed had power and lighting together with a minimum size of 1.0 copper. The first amendment split them taking power up to 1.5.
 
There is no specific answer as it depends on who made the item in question.

Miele said

Thank you for taking the time to contact us with your enquiry about changing a moulded plug.
Yes you can take the plug off without invalidating the warranty, as long as it is connected by a qualified electrician.


Samsung said

Thank you for your email.
This is to acknowledge that we have received your email. In reference to your query, kindly be advised that the designs of our products are made based on market preferences and have undergone series of tests before it is being decided by our Samsung design team and engineers. Thus, changing/altering parts of the unit will automatically void its warranty.
As I said some will try it on. Samsung is one of them.
 