Although 1.5mm cable could take this load, what about light fittings, pendants, fans etc ?
I think this should be coded 2 on a PIR ?
I think this should be coded 2 on a PIR ?
What's the issue? We have a socket rated 13A on a 32A ring?Although 1.5mm cable could take this load, what about light fittings, pendants, fans etc ?I think this should be coded 2 on a PIR ?
Thing is though a light fitting will only draw the current it needs to operateIf it IS a lighting circuit, then, unless the connected accesories are capable of withstanding (20AX switches etc.), then I`d code 2 it mate.HOWEVER, if it was designed to work like that, (which is where sight of the EIC would help), then it would be a case of verifying that the luminaires & switches have not been altered, or the circuit extended with 1.0.
Zs could be an issue, too.
KME
edit: `pache: most domestic light switches are rated 5A, though 10 and 20 are not unheard of. The 13A limit is provided by the fuse in the plug - it isn`t possible to draw 32A from a double socket, OR expect the switch to make/break that sort of current. Yes?
It's the same as a plug top fuse it is there to protect the cable and not the appliance.I asked my college tutor a similar thing and, he turned around and said the mcb is there to protect the cable, so as long as the cable can withstand the rating on the mcb then it is ok. is that correct?
Can I ask where that piece of info comes froim mate? I wasn`t aware of that.It's the same as a plug top fuse it is there to protect the cable and not the appliance.
559.6.1.6
what does it say?its almost like they wrote that reg simply for this post.