5s for distribution and final circuit supplying only stationary equipmentiirc in 17th all circuits upto 32a are now required to have .4sec dt. even fixed equipment and lighting?but what was the 16th ?
yes, for 230v. see table 41.1 (page 46) for other voltages & timesthx andy.and now ALL final circuits are .4 unless above 32a?
they were lowered based on 230v, the old 16th values were 240vSorry, should be Zs.
Voltage is now 230 and not 240 that is why thet have been lowered.Maximum Ze has been lowered in the 17th as well.
Really?!Voltage is now 230 and not 240 that is why thet have been lowered.
Hello cj's have you been on holiday.Zs calculation 16th 240 divided by trip current B6 = 30 amps x .75
17th 230 divided by trip current B6 = 30 amps x .80
so
16th Zs 240/30x.75= 6.00 ohms
17th Zs 230/30x.80= 6.13 ohms
hope this helps CJS