I've been asked to quote to fit a new storage heater, but it's in a prefabricated bungalow and would be a pig of a job to pull a new cable from the CU, not to mention the possibility of asbestos, and there's no spare capacity in the CU.
So I would like to take a feed from the adjacent bedroom that already has a Dimplex XL24N and run the very short distance to the adjoining wall in surface trunking.
The new room will also have an XL24N. So that would be 2 1.7KW heaters on the same 2.5mm radial fed from a 16A MCB. Making a total load of 14.78A @ 230V
So it's within the rating of the MCB and the cable, just a bit unconventional to fit 2 storage heaters on one radial. What do you guys think?
So I would like to take a feed from the adjacent bedroom that already has a Dimplex XL24N and run the very short distance to the adjoining wall in surface trunking.
The new room will also have an XL24N. So that would be 2 1.7KW heaters on the same 2.5mm radial fed from a 16A MCB. Making a total load of 14.78A @ 230V
So it's within the rating of the MCB and the cable, just a bit unconventional to fit 2 storage heaters on one radial. What do you guys think?