2392 Practical Exam question

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

PGS

Junior Member
Joined
Jan 18, 2010
Messages
13
Reaction score
0
Help

I am taking an exam on Thursday 11th at 2.00pm for C&G 2392 (practical).

My problem is testing of PFC/PSCC and PEFC.

PFC/PSCC is testing between incoming L - N with the installation isolated - no problem.

PEFC is testing on incoming live and earth, but is it the incoming earth or the earth bar with all bonding connectors in place?

Also, for polarity testing on incoming supply, using the same earth as for the PEFC test?

Thanks

PGS

 
Earthing conductor in place when doing PFC test i think mate. Just Ze done with earthing conductor disconnected. If im wrong someone please tell me cheers

 
Earthing conductor in place when doing PFC test i think mate. Just Ze done with earthing conductor disconnected. If im wrong someone please tell me cheers
You are correct . earthing conductor disconnected when doing obtaining Ze . Leave earthing conductor connected when measuring PFC ;)

 
Top