Hi, got an issue with a Y plan system. after the heating has stopped calling for heat I am getting around 30v on the CFH at the boiler - its coming from the orange on the zone valve and also back feeding the white (CH on) with the same voltage. it only does it with the HW off (so 230v down the grey from the programmer. the plumber has replaced the programmer & room stat before calling me ( all wired correctly) and I have replace the zone valve head - no difference. The programmer / tank stat and room stat all appear to be switching correctly, and there is no voltage present on the neutral. anybody else come across this? Back there tomorrow to test wiring etc