Hi, we desperately need help!!
We have installed a approximately 40no 32w high frequency PL Downlighters in a Gym, and it has come to light that when a supply fan on a AHU trips the lights in the gym start dimming over a period of around 5 mins, the lights loose around a third of there brightness.
Please note that these are not a dimmed ballast.
The voltage at the lights before and
after stays the same- 234 volts between line to neutral and earth.
The mechanical control panel which feeds the supply and extract fans is located in a store cupboard within the same gym as the lights, please see the scenario below. Voltage at control panel is 234 volts between all phases to neutral and earth.
Turn off main isolator to control panel- lights do not dim.
Turn off extract fan from 3 pole mcb within the control panel- the lights do not dim.
Turn off supply fan from 3 pole mcb within the control panel- the lights in the gym start to dim gradually.
Initially our thoughts were that the extract motor was inducing some form of harmonics down the line and consequently affecting the lights, this does not seem to be the case as we have swapped the motors and still have the same senario.
I don't think that the temperature within the gym is changing drastically to affect the ambient temperature around the lamps. The lamps are low amalgam. But can't rule this out.
The health club are now threatening to close the gym, but we simply don't have any answers.
You thoughts on this would be greatly appreciated.
Craig
We have installed a approximately 40no 32w high frequency PL Downlighters in a Gym, and it has come to light that when a supply fan on a AHU trips the lights in the gym start dimming over a period of around 5 mins, the lights loose around a third of there brightness.
Please note that these are not a dimmed ballast.
The voltage at the lights before and
after stays the same- 234 volts between line to neutral and earth.
The mechanical control panel which feeds the supply and extract fans is located in a store cupboard within the same gym as the lights, please see the scenario below. Voltage at control panel is 234 volts between all phases to neutral and earth.
Turn off main isolator to control panel- lights do not dim.
Turn off extract fan from 3 pole mcb within the control panel- the lights do not dim.
Turn off supply fan from 3 pole mcb within the control panel- the lights in the gym start to dim gradually.
Initially our thoughts were that the extract motor was inducing some form of harmonics down the line and consequently affecting the lights, this does not seem to be the case as we have swapped the motors and still have the same senario.
I don't think that the temperature within the gym is changing drastically to affect the ambient temperature around the lamps. The lamps are low amalgam. But can't rule this out.
The health club are now threatening to close the gym, but we simply don't have any answers.
You thoughts on this would be greatly appreciated.
Craig