I would have to guess that your title means 4D3A?
These are what the table says, single core armoured cables, copper conductors, thermoplastic insulated rated @ 70 deg C, with non magnetic armour.
I don't understand what you mean by "just armoured with no armourings inside them"?
That statement makes no sense to me.
You will probably find that most of the armoured cables you use will be 90 deg C rated, XLPE to BS5467 rather than PVC to BS 6724, it is just that you can't use them at this rating as it is doubtful your terminations will be rated @ 90 deg C.
Again not sure what you mean, will you ever need them?
You will need them if you use the cables to which these tables refer.