can a 4mm radial supply sks from a ring cct
Can't think of any reg you would be breaking, no different than both legs of a ring down the same conduit.anybody know the answer to the multi core question can it be done within the regs
anybody know the answer to the multi core question can it be done within the regs
No its not that easy. What reg numbers are you refering to ? Also see post #9 above. Have a look at 433.1.Hi all,
The regs, and their accompanying diagram make it all perfectly clear...
Unfused spur; "An unfused spur should feed one single or one twin socket-outlet only" Soooo, that is the end of the argument!!
As regards fused spurs, according to the regs and the diagram, they can be used to do a few different things [including fixed equipment], but the killer is, it clearly states " Fused connection unit [FCU] to BS 1363-4" ----- "maximum fuse 13A"
So, that is the end of that then!!!
john...
that's for 2.5mm spur off ring not 4mm, so not perfectly clear.Hi all,
The regs, and their accompanying diagram make it all perfectly clear...
Unfused spur; "An unfused spur should feed one single or one twin socket-outlet only" Soooo, that is the end of the argument!!
john...