Hi Steps,
I do not think there is anything that specifically says you coulod not feed a CU from a RF, but they DO say the following;
The load current in any part of the circuit should be unlikely to exceed for long periods the current-carrying capacity of the cable. This can generally be achieved by;
1, Locating socket-outlets to provide reasonable sharing of the load around the ring.
2, Not supplying immersion heaters, comprehensive electric space heating or loads of a similar profile from the ring circuit.
3, Connecting cookers, ovens and hobs with a rated power exceeding 2kW on their own dedicated radial circuit.
I think the idea is, as you have stated, to avoid a badly unbalanced ring...
I suppose you could fit a CU with a 16A MCB as you have suggested, but you would only be 3A better off than you would by using a BS1363 FCU. Still, the CU would make a handy junction box!!!
I would just go for a 13A fused spur, and then at least there is no question that it complies.. Explain to the client that this means that they are somewhat limited [more in theory than in practice] as to what they will be able to run in there, but if they really do envisage large load then they will have to have a dedicated 4mm 32A radial run out there.
I think i would just extend the ring myself if this were possible.
john...
I do not think there is anything that specifically says you coulod not feed a CU from a RF, but they DO say the following;
The load current in any part of the circuit should be unlikely to exceed for long periods the current-carrying capacity of the cable. This can generally be achieved by;
1, Locating socket-outlets to provide reasonable sharing of the load around the ring.
2, Not supplying immersion heaters, comprehensive electric space heating or loads of a similar profile from the ring circuit.
3, Connecting cookers, ovens and hobs with a rated power exceeding 2kW on their own dedicated radial circuit.
I think the idea is, as you have stated, to avoid a badly unbalanced ring...
I suppose you could fit a CU with a 16A MCB as you have suggested, but you would only be 3A better off than you would by using a BS1363 FCU. Still, the CU would make a handy junction box!!!
I would just go for a 13A fused spur, and then at least there is no question that it complies.. Explain to the client that this means that they are somewhat limited [more in theory than in practice] as to what they will be able to run in there, but if they really do envisage large load then they will have to have a dedicated 4mm 32A radial run out there.
I think i would just extend the ring myself if this were possible.
john...