Just don't use Volex, u'll struggle to get them in. They're crap.Depends on accessory manufacturer bud, the likes of MK isnt a problem.AndyGuinness
GS
Just don't use Volex, u'll struggle to get them in. They're crap.Depends on accessory manufacturer bud, the likes of MK isnt a problem.AndyGuinness
Would you like to re-read this part of your post?The 27A capacity for a 2.5 mm conductor applies for a radial only
You didnt read my 1st post on the thread then SW ? ?:|Volti,Good point, that had not even crossed my mind when I posted my comments earlier about 4mm rings!
So there folks is another reason, and probably more common in domestic, thus probably more worthy of consideration.
a RFC consists of a cable (2.5) that can only carry 27a at most being protected by a 32a protective device (usually)I am not convinced with using 20 amp radials the way I see it ring mains have been used for the last 50 odd years and I can't remember having problems with one being overloaded but I have had customers say they have had 20amp circuit breakers trip when vacuum cleaners are plugged in not commen I admit but a few times I have been told this. I would imagine its because the starting of the vacuum the 20 amp breaker cannot withstand the motor current start up. I cannot see the advantage of 20 amp radials and will carry on using ring mains unless there is a real convincing argument to say they should not be used.
where does this little nugget of information come from?The 27A capacity for a 2.5 mm conductor applies for a radial only this is much higher when its wired in a ring otherwise we wouldnt protect such circuits with a 32a rcbo.Only time it would be a problem is if there is ever a break in the ring then you would have 2 radials on a 32a breaker not giving the cable the protection it needs.As mentioned before the only time 4mm would be used is where there is thermal insulation not neccesarily the whole ring only where it passes through the thermal insulation
Do you not have two cables at each outlet and all around circuit so that is up to 54 amp capacity?a RFC consists of a cable (2.5) that can only carry 27a at most being protected by a 32a protective device (usually)where does this little nugget of information come from?
You didn't mention it specifically.You didnt read my 1st post on the thread then SW ? ?:|