no, its not parallel conductorsDo you not have two cables at each outlet and all around circuit so that is up to 54 amp capacity?
no, its not parallel conductorsDo you not have two cables at each outlet and all around circuit so that is up to 54 amp capacity?
Did I need to Volti ?You didn't mention it specifically.
Seems clear enough to me.Did I need to Volti ? I stated : Does your method of installation require it...rating factors etc ? Would you not agree thermal insulation factors fall within this category ?
Did you now?The total load splits down each leg of the ring meaning that no one leg will ever take the full load so even when the breaker is near its limit the 2.5 mm cables are well within theirs!
sorry Steptoe thought this was common knowledge!
I wouldn't disagree with that, but all I said was you didn't specifically mention that factor and you didn't, hence the reason Sidewinder maybe missed it.Did I need to Volti ? I stated : Does your method of installation require it...rating factors etc ? Would you not agree thermal insulation factors fall within this category ?
yes, the path of least resistance will usually be the shortest path(though not always,) therefore you could in theory have 2X13A loads plugged into the first double socket on the ring, shortest route/least resistance will be via the one leg of the ring straight back to the CU....... = 26A before you apply any other load, plus the fact 27A capacity is under ideal conditions.oh i thought that current took the path of least resistance so depending on where on the ring it was plugged in determined which leg it came back on! im sure you'll correct me if im wrong though! lol
Wet FishThen:The total load splits down each leg of the ring meaning that no one leg will ever take the full load so even when the breaker is near its limit the 2.5 mm cables are well within theirs!
sorry Steptoe thought this was common knowledge!
Wet FishWet Fisherm.......I`m confused now!oh i thought that current took the path of least resistance so depending on where on the ring it was plugged in determined which leg it came back on! im sure you'll correct me if im wrong though! lol
:Applaud :Applaud:Applaud:Applaud:Applaudopcornyes, the path of least resistance will usually be the shortest path(though not always,) therefore you could in theory have 2X13A loads plugged into the first double socket on the ring, shortest route/least resistance will be via the one leg of the ring straight back to the CU....... = 26A before you apply any other load, plus the fact 27A capacity is under ideal conditions.of course, none of this is taking into account a fault/diy Bob and the broken ring scenario.
Hi Volti. by virtue of the fact that I didnt mention any particular Rating Factor; must by defenition mean that I was referring to the requirement to consider All of them, that of course includes Thermal.I wouldn't disagree with that, but all I said was you didn't specifically mention that factor and you didn't, hence the reason Sidewinder maybe missed it.