Hi Folks,
Would welcome input/advice on the following:
Started working on a house which looks like it's been rewired probably within the last 3 yrs.
TT sytem: New'ish CU (S-Type RCD main Sw + RCD protecting 3 rings - up/dwn & kitchen. Lights, bonding all check-out ok!
Both Up & dwn rings check-out great - both have good R1/Rn & R2 readings. R1+R2 + Ze giving max Zs readings well under 7671 requirements for type 'B' MCB's. Insulation >200 & RCD trips @ 12mS.
Issue is with the kitchen ring! R1/Rn & R2 all look good. R1+R2 appears ok. Insulation >200, BUT upon testing the the RCD, my Diolog tester indicates a >50v present and I cannot acquire a trip time? The RCD trips but as said I cannot record a trip time?
I look fwd to any advice .......
Rgds,
JimG.