Won't work,as both will tripactually was considering replacing the wall fuse spurs with ones with RCDs, to see if prevented the unit tripping,
Won't work,as both will tripactually was considering replacing the wall fuse spurs with ones with RCDs, to see if prevented the unit tripping,
missed thisI think you're looking at damp ingress.
Thanks, how should I specify the scope I want covered and ensure its thorough enough without being over the top and flushing money awayBe very careful selecting a person and the scope of your EICR , or you might as well set fire to a pile of £10 notes
I'm not sure an eicr is the correct route.
Investigating the tripping is more important imho
Wouldn't the EICR pick up and hopefully find root of the tripping though?
ok, so to revert back to my issue. what would you suggest I ask of my electrician to find the root of the intermittent issue given it may not present itself when they comeIf you are very lucky it may report low insulation resistance in the property and it would be coded C2 but it wouldn't find and resolve it
Unless you give the spark a blank cheque to report, locate and fix.
Sorry if this isn't what you want to hear,
ok, so to revert back to my issue. what would you suggest I ask of my electrician to find the root of the intermittent issue given it may not present itself when they come
So need to start somewhere and from other's suggestions no harm with EICR to see if any obvious issues with the systemThat unfortunately is the position you are in.
Houses are like modern cars, a devil to fault find and fix.
New house, 15 yeas oldI share the view that inviting an EICR is likely to invite all sorts of faults and recommendations not directly related to your fault.
I would just get an electrician to solve the RCD tripping. That will involve some testing of the circuits and testing the RCD itself, that is all.
By the way what sort of house old or new etc.
Don't be too pessimistic. From what I'm reading I suspect you have an earth leakage fault somewhere. Probably neutral to earth. It could be water in an outside light, deteriorating element in any heating device, or many other faults, or a combination of two or more, but NOT difficult to detect with test gear, and not too difficult to trace by a skilled electrician. The variability you observe is most likely load dependant, rather than a manifestation of Sod's Law. For instance your UF heating WILL draw more current when it's cold, but that could be a complete red herring if the fault is elsewhere, such in your cooker, immersion heater, etc, etc.New house, 15 yeas old
Fingers crossed when electrician comes the system is having one of the days it is tripping so can see it for himself rather than take my word that there is an issue. Already explained the problem and if doesnt trip i dont think I would be wasting their time, my time or the money for the sake of it
Don't bother with the EICR ...concentrate on the tripping problem . First thing to do is to run tests on the RCD to ensure it's not "Nuisance " tripping .no harm with EICR to see if any obvious issues with the system
With regards to inspection, never I suspect. The house is around 15 years old, the kitchen was replaced 3 years ago when the underfloor heating was installed and the electrics were wired up. I've never heard of having reports on household electrics.
Don't bother with the EICR ...concentrate on the tripping problem .