never fitted them before but 5A docket on 6A breaker?????????

Any other tips would be welcome

 
its like a double socket on a 20amp breaker (2 x 13A)

The likelyhood is that your going to have a 60w (0.26A) lamp in the light fitting.

 
but 5A docket on 6A breaker?????????
The old Wiring Regs. from when BS546 sockets were commonplace specified that a 5A socket could be wired on a branch circuit rated up to 15A maximum. The assumed demand on a 5A socket was to be 5A (surprise!), meaning that in theory three 5A sockets could be wired on a 15A circuit, although in practice many installations ended up with more than that for convenience, with loading extremely unlikely to be 5A on every socket due to diversity.

The specified demand for 2A sockets, which were more intended for use on lighting circuits, was "at least 0.5 ampere."

 