4mm would be fine, 6mm would be great, and 10mm would be even better, for current rating and VD purposes with that load and run length. BUT, i suspect it will all come down to R1 + R2 in the end..
Just remember, does the charger have a great big transformer in it?? What MCB will you need,, A "B" or a "C" or even a "D"..
This will be the deciding factor i suspect. not the load or anything else, so as a first move i would be asking the makers what sort of OCPD they recommend..
Completely forget the load, it is the OCPD chosen that you have to design your cable around..
Another thing, earthing type??