Not sure why you are saying something has to change??any way...
as Apache said.. Mira Sport? what power rating is it?
e.g...
http://www.mirashowers.co.uk/onlinecatalog/results.htm?sectionName=Electrichttp://www.mirashowers.co.uk/onlinecatalog/results.htm?sectionName=Electric showers&filter[bRAND_NAME]=Sport
6.0mm cable, clipped direct could carry 47Amps...
table 6F page 134 on-site guide..
And according to table 7.1 page 50 on-site-guide
a 40Amp 6.0mm circuit (inst method C) can be upto 40m long!
so 40amp MCB could provide power for 40x230 = 9.2kWatt.
So if your cable is clipped direct, the run is less than 40m
and the shower is 9.0kw or less...
what needs to change??