oops sort of bludgeoned into this thread didn't i.Are you asking a question there somewhere?
nice use of micro symbolWell, 6 uA is not going to trip an RCD, so first check the functioning of the RCD in isolation, and if it's OK, use an earth leakage clamp meter on each circuit's line and neutral together, to find out which circuit has a high earth leakage, then unplug each appliance on that circuit in turn till you find out which one was causing the high earth leakage.
whilst it may read at X ohms now, but it reduce to much less (or more) depending on movement or dampness, and trip your RCDmight have to just never thought it could be the reason
Yes, that way you measure the difference in current, just the way that the RCD does. However the clamp meter must be able to measure from mA's upwards. Most clamp meters aren't sensitive enough.Sorry for being a bit green here.Do you clamp the meter around the live and neutral of the circuit being investigated.
It's a u. This is a micro symbol,
Looking at the DiLOG DL6507. seems pretty reasonble.