a while back did cu change and installed rod.
it about an hour away so the guy called some one local when his shower or tumble dryer are on the rcd trips. the local guy has no test equipment with him and says the rcd is too sensertive and advises replacement.
so he rings me to come out as i fitted the cu so its under warrenty.
got there and ramp tested with loads connected on a socket, >51ma
flicked to loop test and go about 0.4 ohms
the rod i put in had an ra of about 50 ohms, tested the rod, 42 ohms.
tested the rcd in isolation triped at 25ma, tested at board with neutrals connected >51ma.
so i ir the shower and ring final, E N short on the ring. he said he has had no work done to that circuit and has not been hammering nails in around the sockets. so i narrowed it down between 2 sockets and above one was 2 pics hanning on nails pulled nail out and the fault cleared. pulled new cable through and all working.
so when ramp testing with neutrels connected the current was drawn throught the meter throught the earth bar through the ring cpc N E short then back through the rcd with no imbalance so did not trip?
the low zs on the ring again the current passes through cpc to neutral, so return path is the neutral?
think that explains it?
what do you guys think thanks
it about an hour away so the guy called some one local when his shower or tumble dryer are on the rcd trips. the local guy has no test equipment with him and says the rcd is too sensertive and advises replacement.
so he rings me to come out as i fitted the cu so its under warrenty.
got there and ramp tested with loads connected on a socket, >51ma
flicked to loop test and go about 0.4 ohms
the rod i put in had an ra of about 50 ohms, tested the rod, 42 ohms.
tested the rcd in isolation triped at 25ma, tested at board with neutrals connected >51ma.
so i ir the shower and ring final, E N short on the ring. he said he has had no work done to that circuit and has not been hammering nails in around the sockets. so i narrowed it down between 2 sockets and above one was 2 pics hanning on nails pulled nail out and the fault cleared. pulled new cable through and all working.
so when ramp testing with neutrels connected the current was drawn throught the meter throught the earth bar through the ring cpc N E short then back through the rcd with no imbalance so did not trip?
the low zs on the ring again the current passes through cpc to neutral, so return path is the neutral?
think that explains it?
what do you guys think thanks