Been to a job where they have the following:
2.5mm 4 core SWA at the DB. The four cores are connected as two radial circuits, cores 1 & 2 are fed from MCB 'X' 20A and cores 3 & 4 are fed from MCB 'Y' 15A, the steel wire armour is being used as the cpc for both circuits, the SWA has been earthed at the DB by a brass gland and lock nut to the top gland plate with no flying earth/banjo.
The other end of the SWA 39m away has been made off into a rotary isolator (radial 1), a 2nd rotary isolator is coupled to the 1st isolator (radial 2 not used).
The 1st Isolator then feeds a 12m dado trunking below some metal benches all wired in 2.5mm T&E. This is connected to 14 switched FCU equally spaced along the trunking.
Each FCU has a four gang 13amp plug adapter connected to the load side via a flexible cable, into each of these is a PC + monitor, label printer and scales.
I was there to quote to do a mirror image of the setup on the opposite side of the 12m belt conveyor belt so they can have 28 stations chucking mail onto the conveyor.
The issues are:
1. High Protective Conductor Current (HPCC) and the failure to have earths in separate terminals at all points in the circuit.
2. No second cpc or suitably sized single cpc.
3. 4 Gang adapters don
2.5mm 4 core SWA at the DB. The four cores are connected as two radial circuits, cores 1 & 2 are fed from MCB 'X' 20A and cores 3 & 4 are fed from MCB 'Y' 15A, the steel wire armour is being used as the cpc for both circuits, the SWA has been earthed at the DB by a brass gland and lock nut to the top gland plate with no flying earth/banjo.
The other end of the SWA 39m away has been made off into a rotary isolator (radial 1), a 2nd rotary isolator is coupled to the 1st isolator (radial 2 not used).
The 1st Isolator then feeds a 12m dado trunking below some metal benches all wired in 2.5mm T&E. This is connected to 14 switched FCU equally spaced along the trunking.
Each FCU has a four gang 13amp plug adapter connected to the load side via a flexible cable, into each of these is a PC + monitor, label printer and scales.
I was there to quote to do a mirror image of the setup on the opposite side of the 12m belt conveyor belt so they can have 28 stations chucking mail onto the conveyor.
The issues are:
1. High Protective Conductor Current (HPCC) and the failure to have earths in separate terminals at all points in the circuit.
2. No second cpc or suitably sized single cpc.
3. 4 Gang adapters don