You mean RCCD? Are you sure its tripping due to current and not another reason like termal effects? They are rated in the same way a JB or light switch is in that it won't protect from over current but has only been designed to work up to that maximum current.all in the title i think.hard to imagine that with the feel of a mcb in the way it turns on/off that they won't be rcbo's?
i ask as i have a rcd to en61008 that does trip with excessive load!
I think you are confusing yourself there. There is no device called an RCD. Its a "class" of devices that both an RCCD and RCBO (along with SRCD, PRCD and SRCB) are members of.so an rccd is a rcd?i.e with no overload protection
i can't see it being
rccd= fault protection only or overload protection only
where
rcd= no fault or overload protection
rcbo= fault & overload protection
+1I think you are confusing yourself there. There is no device called an RCD. Its a "class" of devices that both an RCCD and RCBO (along with SRCD, PRCD and SRCB) are members of.
Normal circuit theory says they must have.Earth faults (L-E or N-E) have nothing to do with the load attached to the circuit..
thats wrong adsNormal circuit theory says they must have.Current in a series circuit remains constant throughout.
If you introduce a N - E fault, you are introducing a parallel path back.
Current in a parallel circuit will split down each leg of the parallel path in proportion to the resistance of each leg.
If the resistance of the two paths remains the same, and you increase the current (the load), then it stands to reason that the current down each parallel return will increase.
So, circuit current - 10 A.........N - E leakage 15 mA
circuit current - 20 A.........N - E leakage 30mA
So how much leakage will there be, exactly, in a circuit with a N - E faultthats wrong adsthe leak will only draw what ever current is drawn due to its resistance value
regardless of the load.
there has to be some load but how much is irrelevantSo how much leakage will there be, exactly, in a circuit with a N - E fault