Not sure about that but you may get a tingle from the bathroom taps.A N fault on PME would lead to the lights dimming every time you turned the kettle on and would be bloody obvious.
as it should be,It only happens on T N CS supplies that don't have an earth rod at the premises. It wouldn't happen in my country because all houses with PME'd supplies each have their own earth spike.
I suspect that you're thinking of the old voltage operated earth leakage circuit breakers (VOELCB). These became obsolescent more than 30 years ago....But somewhere hidden in a wall or beneath a floor there must be a connection from the current lighting earth to the earth of the ring main. This is going to cause all sorts of fun and games for RCD protecting the lighting circuit isnt it?
Another quandry.. how do electric/plumbed towel rails ever work? A fault could surely cause currently to flow back to earth through the HW pipe bonding (not through the CU) or back through the RCD protected circuit? Is the theory that both routes to earth would be paths of equal resistance hence enough current would flow back through the CU to trip the RCD? ..or should I stop thinking about this having far exceeded by GCSE electrics?
I don't understand, you have found a fault which could cause the symptoms you described if the lighting circuit was supplementary bonded to the water pipes (which it should have been, since there is no rcd protection to all circuits in the bathroom).The fact that the earth is not continuous in the lighting circuit is a problem, but only if you have metal fittings.First electrician has been round to have a look. His verdict is the only problem is a lack of Earth on the lighting circuit. Proposed fix - replacement of 2 lighting circuits across 3 floors and new fully RCD protected CU. Explanation of live metalware in the bathroom - likely caused by a combination of no lighting earth coupled with some conductivity of the walls combined with notoriously inaccurate voltage pen.
First electrician has been round to have a look. His verdict is the only problem is a lack of Earth on the lighting circuit. Proposed fix - replacement of 2 lighting circuits across 3 floors and new fully RCD protected CU. Explanation of live metalware in the bathroom - likely caused by a combination of no lighting earth coupled with some conductivity of the walls combined with notoriously inaccurate voltage pen.
I don't understand, you have found a fault which could cause the symptoms you described if the lighting circuit was supplementary bonded to the water pipes (which it should have been, since there is no rcd protection to all circuits in the bathroom).
The fact that the earth is not continuous in the lighting circuit is a problem, but only if you have metal fittings.
It could be that the earth cable has worked loose in just one fitting and it could be fixed.
The lighting circuit mcb could then be changed to an rcbo.
It just needs a bit of thorough testing, surely.
Instead, you have been quoted 2 new circuits, with new fittings presumably, and a whole new CU. ££££
Let's hope the other sparky comes up with a cheaper alternative.
Indeed we do have 2 metal wall-lights in the bathroom. The casing screw on one had pierced the live which is, I believe, what caused the other metalware in the bathroom to go live. Having fixed the casing of the light - the taps etc are no longer giving me a shock / showing live.I don't understand, you have found a fault which could cause the symptoms you described if the lighting circuit was supplementary bonded to the water pipes (which it should have been, since there is no rcd protection to all circuits in the bathroom).
The fact that the earth is not continuous in the lighting circuit is a problem, but only if you have metal fittings.
It could be that the earth cable has worked loose in just one fitting and it could be fixed.
The lighting circuit mcb could then be changed to an rcbo...
Not being able to sign off! What bull shxt. The electrician writes the description of the works the cert covers. Nothing more. Nothing less. Best you try another spark.Indeed we do have 2 metal wall-lights in the bathroom. The casing screw on one had pierced the live which is, I believe, what caused the other metalware in the bathroom to go live. Having fixed the casing of the light - the taps etc are no longer giving me a shock / showing live.
The house is an edwardian property on 3 floors. There are 3 separate RCD protected rings for the sockets (1 per floor) and 2 lighting circuits (not RCD protected). 1 Covering the ground floor, 1 covering the top 2 floors.
Throughout the house there are a selection of metal light fittings and metal switches with no earthing present on any of the lighting circuits.
The bathroom lights and switch has an earth cable present.
The electrician who came yesterday had the view that the only way to resolve the problem was to add a proper earth to the lighting ring on the top floor. Regardless of whether this would fix the problem, this sounds like a sensible idea to me seeing as we are redecorating currently top-down. My question to him was whether a new circuit could be created for the top floor lighting and a new breaker added to the CU (plenty of spare slots). This would allow us to uprate the 1st and ground floors at a later date when we start the decorating there. His view was that he would be unable to do this since he could not sign off the work with the remaining 2 floors having no earth, and so he would only quote for 'all or nothing'. Is this correct? I thought that as long as the current system was being improved or made no-worse then that was basically ok?
Waiting on a time for the 2nd guy now
Once again - thanks all for your advice and guidance