Guys can you give me some advice on the items below as this Part P confuses me sometimes.
1) client wants bathroom fan changing has no isolator on fan supply from light switch and CU not RCD protected.
I intended to replace Fan and install pull switch as isolation switch do i need to rcd protect as i have changed circuit and is it notifiable have assesment soon so need to get it right.
2) Client installing under floor heating mat I am aware thermostat not allowed in bathroom and has to be rcd protected does it need to be seperate circuit or can you spur from ring which is rcd protected to clock and thermostat in external position to bathroom.