A 230v 4.5Kw load is supplied using single core 70 degrees c thermoplastic cables in conduit, the protection device is a BS 88 type 2 ,length of circuit is 25m and ambient temp is 35 degrees c

a)calc design current

b)the min fuse rating

c)correction factors that apply

d)minimum cable rating

e)cable size

f)actual voltdrop

good for revision

i'l put my workings out up later

 
no what he hopes is someone brainy person will do all the work for him to get the answer in class correct in the mornind :^O :^O :^O

JOKE BY THE WAY BEFORE ANY SLAPS ON THE WRISTS ARE HANDED OUT :(

 
no what he hopes is someone brainy person will do all the work for him to get the answer in class correct in the mornind :^O :^O :^O JOKE BY THE WAY BEFORE ANY SLAPS ON THE WRISTS ARE HANDED OUT :(
Ib=19.56

In=20amp

ca 0.94 cg 1.00

ci =n/a cc = n/a

Iz = 21.7a

cable size 2.5mm

vd= 8.8v

 