While having a pint and a chat with a friend of mine who is also a sparks, I was told that a friend of his (carrying out tenanted, initial verifications for the council) was not meauring Ze but using the calculation:- Zs - (r1+r2)= Ze. I know that this is not allowed and as I have the NICEIC Inspection and Testing book, which backs me up I showed him. However the book does not state why it is not allowed and I just wondered what others view were on this?
To stick a bit more padding around 'Sir Noz's' quite correct answer I will add the following for you to consider......
(i)
Water and Gas pipes etc.. are NOT permitted as a means of earthing...
see regulation 542.2.4 pg 127
(ii)
You have got to have means to measure the resistance of the earthing arrangements....
see regulation 542.4.2 pg 128
So.. it leaves the question....
How are you going to prove that the resistance of the earthing arrangments are adequate for the type of earth method employed on that installtion...
Without disconnecting ALL possible parallel paths...
You could have a situation where a main electrical earth connection has come adrift, but you are getting a reasonable resistance down through the gas and/or water piper via the central heating system etc...
Which obviously don't comply with regs due to 542.2.4
but if you do Ze=Zs-(R1+R2) you could put an apparent compliant Ze value on you cert signing it to say it all is up to BS7671.. which it isn't....
If you can prove there are NO extraneous metal parts on the installation..
e.g. plastic water pipe coming in, No gas No oil etc.. then the calculation Ze=Zs-(R1+R2) would be quite accurate
otherwise you can only measure Ze directly across the supply with the installation disconnected