But the EIC is issued for the consumer unit - that's what you are installing.A cu change has to be certificated with an installation certificate so all tests in sequence+ if your connecting circuits wouldn't you want to know everything was A ok before you power up ?
Why would you issue a complete eic for a consumer unit change you have to be very careful doing this as you have only changed the circuit protective device and possibly an RCD. An eic is for a new circuit you have not installed a new circuit just the protective device.The EIC with Schedule of inspections and Schedule of test results covers the CU change no need for a PIR as its all coverd on the EIC which has to be completed for a CU change! A PIR might not even be due when the CU is changed! Different if just adding a new circuit it would be an EIC for that then a PIR for the exising instalation (if it was due) can get confusing though
I'm afraid you are wrong, mate.The EIC with Schedule of inspections and Schedule of test results covers the CU change no need for a PIR as its all coverd on the EIC which has to be completed for a CU change! A PIR might not even be due when the CU is changed! Different if just adding a new circuit it would be an EIC for that then a PIR for the exising instalation (if it was due) can get confusing though
What do you issue for a board change then batty mate?Why would you issue a complete eic for a consumer unit change you have to be very careful doing this as you have only changed the circuit protective device and possibly an RCD. An eic is for a new circuit you have not installed a new circuit just the protective device.
An eic but you must state its for board change only and fill in relevent parts which is loop test at furthest point of circuit and RCD tests also any faults found while testing.What do you issue for a board change then batty mate?
No but generally I ensure its a ring do an insulation test to ensure it won't trip RCD and loop at each socket.So you would connect a ring circuit in without doing the 3 step ring circuit test,polarity tests, insulation resistance r1+r2 etc ?
As it is a domestic property probabily notHere goes1.....First thing i noticed was the Zs values given are bang on ie R1R2 + Ze this makes me think you havenot measured and just calculated.
2....You can put the 5x results in the "other" column but obviously write 5x at the top
3....Serial numbers req for meter
4....Are the luminaires vulnerable in a bungalow, a florry is ok (if it dunt have an electronic starter or gear tray)
5....Presence of diagrams and cct charts. Is there a technical diagram and chart on site?
6...Routing of cables in prescribed zones. Are you sure? if not put LIM
7....Theres no garage so where is the SWA
8....Max demand....A cooker and shower on at the same time...cud this be more than 50? its your call
9....60947-3
10...Alteration not a new installation
11....You have not filled in the amended to date
12...Not filled in the next inspection time
13...Spelled your name wrong( Joke )
14....Did you actually see the main fuse or did you just look at the meter rating or is it intuition.
Thats it i think
.. :coffee
Hi Sanny,So you would connect a ring circuit in without doing the 3 step ring circuit test,polarity tests, insulation resistance r1+r2 etc ?
I know probably not, but he still ticked it as if it hadAs it is a domestic property probabily notImpossible to do as there is no amendment yet, first one does not come out till next year.
I disagree, the test results will be attached to the whole document so page 1 will have the installation address. There is nothing wrong with crossing out address and leaving location of distribution board. If you don't agree check out the Part P doctoron shed of test results i would have put full address of where work was carried out not just in the porch, then maybe write in the porch in comments box
Nothing wrong with calculating, this is acceptable as long as Ze was measured as well as R1 + R2. Lets not have this old debate again.Here goes1.....First thing i noticed was the Zs values given are bang on ie R1R2 + Ze this makes me think you have not measured and just calculated.
And by the same argument when adding an additional accessory to a circuit you only do your tests on the new bit of cable and your new accessory added.. not the whole circuit?But the EIC is issued for the consumer unit - that's what you are installing.So the Schedule of Test Results accompanying the EIC should only have test results relative to the installation of the CU.
The rest of the installation (existing), should be subject to a PIR and the relative test results for said installation recorded on a Schedule of Test Results accompanying the PIR.