If any help I had similar call today."Ring main MCB Tripping every now and then over last few days, getting worse will only stay on 30 secs or so"
(Pre 16th Edition Installation NO RCD on this circuit)
Arrived at 2 PM walked thru property un-plugged all appliances and switched off all Fused connection units, Disconnected Alarm panel N from un-switched spur and removed fuse, re-set MCB and it tripped again soon after.
Disconnected circuit in Consumer Unit did Continuity test of Ring and L to N all Ok (This Confirmed nothing still plugged in or connected to circuit),
Did Insulation Tests L-N 20 M ohm, ok N-E 20 M ohm ok, L-E .001 M ohm.
Diagnosis Low Insulation fault L to Earth.
Went to approx mid point of Ring, double socket in bedroom furthest corner of Bungalow from Mains.
Split Ring and Disconnected SWA taken from this socket to Lamppost in Garden.
Returned to Consumer Unit retested and Fault gone.
Took Meter back to socket position in bedroom and tested SWA to Lamp post- confirmed fault on spur to lamp post. Went to Lamp post opened up to find Fused connection Unit feeding Time switch which was switched Off, no obvious fault IN lamp post confirmed fault in SWA cable.
Customer never uses Lamp post so happy to isolate it.
Chopped SWA cable off in back of socket, put every thing back to-gether, retested Ring continuity and Insulation resistence at C unit, all now + 200 M ohms. Powered up did Loop test at socket in Bedroom and a couple of others.
Had a cup of Tea and chat, suggested up grade to 17th Edition standard, wrote out my invoice, payment in pocket and out of the door at 3PM.
Basic call out charge for 1 Hours Labour, no materials used.
Problem solved and a happy Customer.